The 202U relay working voltage says 20A at 120VAC. Can the relays be wired for this while the wireless receiver unit is powered at 12V? I can’t find a wiring diagram for this but there’s a nice blue terminal block that seems unused. TIA
The relay can switch up to 10A @125Vac load.
The blue terminal is for limit switches, it can’t be connected to any load (or will cause damage to receiver).
Please see relay datasheet for full specs.
https://pdf1.alldatasheet.com/datasheet-pdf/view/1131802/SONGLERELAY/SRA-05VDC-CL.html
Thank you William. As I understand it, the relays switch the input voltage to the NO/NC connectors for each relay. How do I connect 125vac to it so that NC/NO are using 125VAC?
The relay contact are dry contact, it does not switch input voltage.
The relay just act like as simple on/off switch.
Thank you William. I understand. The 202U is a wireless relay for 9-30VDC or 9-24VAC as per the specs and cannot switch 10A @ 120VAC. Correct?
No, the 9-30VDC (9-24VAC) is relay’s power input voltage, so relay can receive wireless signal and turn on/off relays.
It can switch 120Vac, see the wiring photo in manual below.
Ahhhhhh. I get it. Thanks.